Mining Engineering > GATE 2023 > Mine Ventilation
A fan installed in a mine ventilation system circulates 30 m3/s of air to two districts A and B as shown in Figure below. It is desired to increase the quantity of air by 20% in the district B using a booster fan in it. Assuming that the main fan pressure is unchanged, the pressure of the booster fan, in Pa, is ____________. [rounded off to 2 decimal places]


Correct : 138.24
Similar Questions
Identify the WRONG statement: The application of controlled air recirculation in an underground work place can
Identify the WRONG statement: The application of controlled air recirculation in an underground work place can
Identify the WRONG statement: The application of controlled air recirculation in an underground work place can
Total Unique Visitors
Loading......