Electrical Engineering > GATE 2026 > Transformers
A 220V/12V single-phase transformer is designed for use in India and rated 100 VA at 50 Hz. Later, this unit is shipped to the USA where it is used as a 110V/6V transformer at 60 Hz.
Which of the following statements is/are correct?
A
No-load current drawn would be smaller for operation in the USA compared to that in India
B
For the same load current, the losses would be higher in the USA compared to that in India
C
The peak magnetic flux density in the core would be higher while operating in the USA compared to that in India
D
The eddy current losses in the core would be approximately 44% higher while operating in the USA compared to that in India

Correct : a,d

Similar Questions

Which one of the following options represents possible voltage polarities in a single-phase two winding transformer? Here, Vp is the applied primary voltage, Ep...
#99 MCQ
When the winding c-d of the single-phase, 50 Hz, two-winding transformer is supplied from an AC current source of frequency 50 Hz, the rated voltage of 200 V (r...
#199 Fill in the Blanks
In a single-phase transformer, the total iron loss is 2500 W at nominal voltage of 440 V and frequency 50 Hz. The total iron loss is 850 W at 220 V and 25 Hz. T...
#253 MCQ

Related Topics

transformer design India transformer design USA GATE Electrical Engineering 2026 single phase transformer 220V/12V transformer 110V/6V transformer GATE 2026 transformer efficiency India transformer efficiency USA transformer losses India transformer losses USA transformer magnetic flux transformer eddy current losses GATE electrical questions