Electrical Engineering > GATE 2026 > Synchronous Machines
A certain application requires power at a frequency of 16.67 Hz, while the available grid frequency is 50 Hz. A 3-phase synchronous motor connected to the 50 Hz, 3-phase grid, driving a synchronous generator, is used for this application.
Which one of the following combinations is a suitable choice for the number of poles in the motor and generator, respectively?
A
2, 6
B
6, 2
C
4, 6
D
6, 4

Correct : a

Similar Questions

An alternator with internal voltage of 1<δ1 p.u and synchronous reactance of 0.4 p.u is connected by a transmission line of reactance 0.1 p.u to a synchronou...
#240 Fill in the Blanks
The figure below shows the per-phase Open Circuit Characteristics (measured in V) and Short Circuit Characteristics (measured in A) of a 14 kVA, 400 V, 50 Hz, 4...
#318 MCQ
A cylindrical rotor synchronous generator with constant real power output and constant terminal voltage is supplying 100 A current to a 0.9 lagging power factor...
#321 Fill in the Blanks

Related Topics

No tags found

Unique Visitor Count

Total Unique Visitors

Loading......