Electrical Engineering > GATE 2026 > Synchronous Machines
A certain application requires power at a frequency of 16.67 Hz, while the available grid frequency is 50 Hz. A 3-phase synchronous motor connected to the 50 Hz, 3-phase grid, driving a synchronous generator, is used for this application.
Which one of the following combinations is a suitable choice for the number of poles in the motor and generator, respectively?
Which one of the following combinations is a suitable choice for the number of poles in the motor and generator, respectively?
Correct : a