Electrical Engineering > GATE 2026 > Transformers
A 15 kVA, 1100 V/220 V, single-phase two-winding transformer is configured as a 1.32 kV/1.1 kV autotransformer.
What will be the rating of the autotransformer?
What will be the rating of the autotransformer?
Correct : c