Electrical Engineering > GATE 2025 > Economic Dispatch
Two units rated at 100 MW and 150 MW are enabled for economic load dispatch. When the overall incremental cost is 10,000 Rs./MWh, the units are dispatched to 50 MW and 80 MW respectively. At an overall incremental cost of 10,600 Rs./MWh, the power output of the units are 80 MW and 92 MW, respectively. The total plant MW-output (without overloading any unit) at an overall incremental cost of 11,800 Rs./MWh is ______ (round off to the nearest integer).

Correct : 178