Electrical Engineering > GATE 2025 > Power Measurement
In an experiment to measure the active power drawn by a single-phase RL Load connected to an AC source through a 2 Ω resistor, three voltmeters are connected as shown in the figure below. The voltmeter readings are as follows: VSource=200 V, VR=9 V, VLoad=199 V. Assuming perfect resistors and ideal voltmeters, the Load-active power measured in this experiment, in W, is ______ (round off to one decimal place).


Correct : 887.4