Electrical Engineering > GATE 2024 > Transient Stability
The single line diagram of a lossless system is shown in the figure. The system is operating in steady-state at a stable equilibrium point with the power output of the generator being Pmax sin δ, where δ is the load angle and the mechanical power input is 0.5Pmax. A fault occurs on line 2 such that the power output of the generator is less than 0.5Pmax during the fault. After the fault is cleared by opening line 2, the power output of the generator is (Pmax/√2) sin δ. If the critical fault clearing angle is π/2 radians, the accelerating area on the power angle curve is _______ times Pmax. (rounded off to 2 decimal places)


Correct : 0.35