Electrical Engineering > GATE 2024 > Power System Analysis
The figure shows the single line diagram of a 4-bus power network. Branches b1, b2, b3, and b4 have impedances 4z, z, 2z, and 4z per-unit (pu), respectively, where z=r+jx with r>0 and x>0. The current drawn from each load bus (marked as arrows) is equal to I pu, where I≠0. If the network is to operate with minimum loss, the branch that should be opened is _______.
A
b1
B
b2
C
b3
D
b4

Correct : d

Similar Questions

A 3-Bus network is shown. Consider generators as ideal voltage sources. If rows 1, 2 and 3 of the YBus matrix correspond to Bus 1, 2 and 3, respectively, then Y...
#256 MCQ
The figure shows the per-phase representation of a phase-shifting transformer connected between buses 1 and 2, where α is a complex number with non-zero real an...
#514 MCQ
In the following network, the voltage magnitudes at all buses are equal to 1 p.u., the voltage phase angles are very small, and the line resistances are negli...
#960 MCQ

Related Topics

power network analysis single line diagram GATE Electrical Engineering 2024 electrical engineering gate minimum loss network branch impedance GATE 2024 question 19 power network losses electrical engineering losses