A balanced delta connected load consisting of the series connection of one resistor (R=15 Ω) and a capacitor (C=212.21 μF) in each phase is connected to three-phase, 50 Hz, 415 V supply terminals through a line having an inductance of L=31.83 mH per phase, as shown in the figure. Considering the change in the supply terminal voltage with loading to be negligible, the magnitude of the voltage across the terminals VAB in Volts is _______. (Round off to the nearest integer).


Correct : 390