Electrical Engineering > GATE 2023 > Three-Phase Circuits
A balanced delta connected load consisting of the series connection of one resistor (R=15 Ω) and a capacitor (C=212.21 μF) in each phase is connected to three-phase, 50 Hz, 415 V supply terminals through a line having an inductance of L=31.83 mH per phase, as shown in the figure. Considering the change in the supply terminal voltage with loading to be negligible, the magnitude of the voltage across the terminals VAB in Volts is _______. (Round off to the nearest integer).

Correct : 390

Similar Questions

In the circuit shown, Z1=50∠-90° Ω and Z2=200∠-30° Ω. It is supplied by a three-phase 400 V source with the phase sequence being R-Y-B. Assume the wattmeters W1...
#131 Fill in the Blanks
A 3-phase, star-connected, balanced load is supplied from a 3-phase, 400 V (rms), balanced voltage source with phase sequence R-Y-B, as shown in the figure. If...
#185 MCQ
The line currents of a three-phase four wire system are square waves with amplitude of 100 A. These three currents are phase shifted by $120^{\circ}$ with respe...
#365 MCQ