Electrical Engineering > GATE 2023 > Transformers
When the winding c-d of the single-phase, 50 Hz, two-winding transformer is supplied from an AC current source of frequency 50 Hz, the rated voltage of 200 V (rms), 50 Hz is obtained at the open-circuited terminals a-b. The cross-sectional area of the core is 5000 mm2 and the average core length traversed by the mutual flux is 500 mm. The maximum allowable flux density in the core is Bmax=1 Wb/m2 and the relative permeability of the core material is 5000. The leakage impedance of the winding a-b and winding c-d at 50 Hz are (5+j100π×0.16) Ω and (11.25+j100π×0.36) Ω, respectively. Considering the magnetizing characteristics to be linear and neglecting core loss, the self-inductance of the winding a-b in millihenry is _______. (Round off to 1 decimal place).

Correct : 500.0