Electrical Engineering > GATE 2022 > Load Flow
Two generating units rated for 250 MW and 400 MW have governor speed regulations of 6% and 6.4%, respectively, from no load to full load. Both the generating units are operating in parallel to share a load of 500 MW. Assuming free governor action, the load shared in MW, by the 250 MW generating unit is ________. (round off to nearest integer)
Correct : 195
Similar Questions
In the figure, the voltages are π£1(π‘) = 100cos(ππ‘), π£2(π‘) = 100cos(ππ‘ + π/18) and
π£3(π‘) = 100cos(ππ‘ + π/36). The circuit is in sinusoidal steady state, and π
In a load flow problem solved by Newton-Raphson method with polar coordinates, the size of the Jacobian is 100x100. If there are 20 PV buses in addition to PQ b...
In a 100 bus power system, there are 10 generators. In a particular iteration of Newton Raphson load flow technique (in polar coordinates), two of the PV buses...