Electrical Engineering > GATE 2022 > Load Flow
Two generating units rated for 250 MW and 400 MW have governor speed regulations of 6% and 6.4%, respectively, from no load to full load. Both the generating units are operating in parallel to share a load of 500 MW. Assuming free governor action, the load shared in MW, by the 250 MW generating unit is ________. (round off to nearest integer)

Correct : 195

Similar Questions

In the figure, the voltages are 𝑣1(𝑑) = 100cos(πœ”π‘‘), 𝑣2(𝑑) = 100cos(πœ”π‘‘ + πœ‹/18) and 𝑣3(𝑑) = 100cos(πœ”π‘‘ + πœ‹/36). The circuit is in sinusoidal steady state, and 𝑅
#77 MCQ
In a load flow problem solved by Newton-Raphson method with polar coordinates, the size of the Jacobian is 100x100. If there are 20 PV buses in addition to PQ b...
#524 Fill in the Blanks
In a 100 bus power system, there are 10 generators. In a particular iteration of Newton Raphson load flow technique (in polar coordinates), two of the PV buses...
#578 MCQ

Related Topics

parallel generator operation GATE Electrical Engineering 2022 governor speed regulation load sharing parallel generators 250 MW generating unit 400 MW generating unit electrical engineering gate load sharing parallel GATE 2022 question 56