Electrical Engineering > GATE 2022 > Economic Load Dispatch
The fuel cost functions in rupees/hour for two 600 MW thermal power plants are given by
Plant 1: C1 = 350 + 6P1 + 0.004P12
Plant 2: C2 = 450 + aP2 + 0.003P22
where P1 and P2 are power generated by plant 1 and plant 2, respectively, in MW and a is constant. The incremental cost of power (λ) is 8 rupees per MWh. The two thermal power plants together meet a total power demand of 550 MW. The optimal generation of plant 1 and plant 2 in MW, respectively, are
A
200, 350
B
250, 300
C
325, 225
D
350, 200

Correct : b

Similar Questions

Two generators have cost functions F1 and F2. Their incremental-cost characteristics are They need to deliver a combined load of 260 MW. Ignoring the net...
#231 MCQ
Consider the economic dispatch problem for a power plant having two generating units. The fuel costs in Rs/MWh along with the generation limits for the two unit...
#730 NAT
The incremental costs (in Rupees/MWh) of operating two generating units are functions of their respective powers P1 and P2 in MW, and are given by dC1/dP1 = 0.2...
#794 NAT

Related Topics

power generation optimization thermal power plants GATE Electrical Engineering 2022 optimal power generation incremental cost power power demand thermal GATE 2022 EE power generation problem thermal power cost calculation