Electrical Engineering > GATE 2021 > Economic Load Dispatch
Two generators have cost functions F1 and F2. Their incremental-cost characteristics are
They need to deliver a combined load of 260 MW. Ignoring the network losses, for economic operation, the generations P1 and P2 (in MW) are:
A
P1 = P2 = 130
B
P1 = 160, P2 = 100
C
P1 = 140, P2 = 120
D
P1 = 120, P2 = 140

Correct : c

Similar Questions

The fuel cost functions in rupees/hour for two 600 MW thermal power plants are given byPlant 1: C1 = 350 + 6P1 + 0.004P12Plant 2: C2 = 450 + aP2 + 0.003P22where...
#477 MCQ
Consider the economic dispatch problem for a power plant having two generating units. The fuel costs in Rs/MWh along with the generation limits for the two unit...
#730 NAT
The incremental costs (in Rupees/MWh) of operating two generating units are functions of their respective powers P1 and P2 in MW, and are given by dC1/dP1 = 0.2...
#794 NAT