Electrical Engineering > GATE 2020 > Synchronous Generators
A three-phase cylindrical rotor synchronous generator has a synchronous reactance XS and a negligible armature resistance. The magnitude of per phase terminal voltage is VA and the magnitude of per phase induced emf is EA. Considering the following two statements, P and Q,
P: For any three-phase balanced leading load connected across the terminals of this synchronous generator, VA is always more than EA.
Q: For any three-phase balanced lagging load connected across the terminals of this synchronous generator, VA is always less than EA.
which of the following options is correct?
A
P is false and Q is true.
B
P is true and Q is false.
C
P is false and Q is false.
D
P is true and Q is true.

Correct : a