Electrical Engineering > GATE 2020 > Synchronous Generators
A three-phase cylindrical rotor synchronous generator has a synchronous reactance XS and a negligible armature resistance. The magnitude of per phase terminal voltage is VA and the magnitude of per phase induced emf is EA. Considering the following two statements, P and Q,
P: For any three-phase balanced leading load connected across the terminals of this synchronous generator, VA is always more than EA.
Q: For any three-phase balanced lagging load connected across the terminals of this synchronous generator, VA is always less than EA.
which of the following options is correct?
P: For any three-phase balanced leading load connected across the terminals of this synchronous generator, VA is always more than EA.
Q: For any three-phase balanced lagging load connected across the terminals of this synchronous generator, VA is always less than EA.
which of the following options is correct?
Correct : a
Similar Questions
A 3-phase, 11 kV, 10 MVA synchronous generator is connected to an inductive load of power factor (β3/2) via a lossless line with a per-phase inductive reactance...
A single 50 Hz synchronous generator on droop control was delivering 100 MW power to a system. Due to increase in load, generator power had to be increased by 1...
A 25 kVA, 400 V, Ξ-connected, 3-phase, cylindrical rotor synchronous generator requires a field current of 5 A to maintain the rated armature current under shor...