Electrical Engineering > GATE 2020 > Synchronous Machines
A cylindrical rotor synchronous generator has steady state synchronous reactance of 0.7 pu and subtransient reactance of 0.2 pu. It is operating at (1+j0) pu terminal voltage with an internal emf of (1+j0.7) pu. Following a three-phase solid short circuit fault at the terminal of the generator, the magnitude of the subtransient internal emf (rounded off to 2 decimal places) is _______ pu.

Correct : 1.01 to 1.03