Electrical Engineering > GATE 2020 > Synchronous Machines
A cylindrical rotor synchronous generator with constant real power output and constant terminal voltage is supplying 100 A current to a 0.9 lagging power factor load. An ideal reactor is now connected in parallel with the load, as a result of which the total lagging reactive power requirement of the load is twice the previous value while the real power remains unchanged. The armature current is now _______ A (rounded off to 2 decimal places).

Correct : 123.00 to 127.00

Similar Questions

An alternator with internal voltage of 1<δ1 p.u and synchronous reactance of 0.4 p.u is connected by a transmission line of reactance 0.1 p.u to a synchronou...
#240 Fill in the Blanks
The figure below shows the per-phase Open Circuit Characteristics (measured in V) and Short Circuit Characteristics (measured in A) of a 14 kVA, 400 V, 50 Hz, 4...
#318 MCQ
A cylindrical rotor synchronous generator has steady state synchronous reactance of 0.7 pu and subtransient reactance of 0.2 pu. It is operating at (1+j0) pu te...
#324 Fill in the Blanks

Related Topics

No tags found

Unique Visitor Count

Total Unique Visitors

Loading......