Electrical Engineering > GATE 2020 > Synchronous Machines
A cylindrical rotor synchronous generator with constant real power output and constant terminal voltage is supplying 100 A current to a 0.9 lagging power factor load. An ideal reactor is now connected in parallel with the load, as a result of which the total lagging reactive power requirement of the load is twice the previous value while the real power remains unchanged. The armature current is now _______ A (rounded off to 2 decimal places).

Correct : 123.00 to 127.00