Electrical Engineering > GATE 2020 > Synchronous Generators
A single 50 Hz synchronous generator on droop control was delivering 100 MW power to a system. Due to increase in load, generator power had to be increased by 10 MW, as a result of which, system frequency dropped to 49.75 Hz. Further increase in load in the system resulted in a frequency of 49.25 Hz. At this condition, the power in MW supplied by the generator is _______ (rounded off to 2 decimal places).

Correct : 123.00 to 135.00