Electrical Engineering > GATE 2020 > Transformers
A single-phase, 4 kVA, 200 V/100 V, 50 Hz transformer with laminated CRGO steel core has rated no-load loss of 450 W. When the high-voltage winding is excited with 160 V, 40 Hz sinusoidal ac supply, the no-load losses are found to be 320 W. When the high-voltage winding of the same transformer is supplied from a 100 V, 25 Hz sinusoidal ac source, the no-load losses will be _______ W (rounded off to 2 decimal places).

Correct : 19.90 to 20.20

Similar Questions

Which one of the following options represents possible voltage polarities in a single-phase two winding transformer? Here, Vp is the applied primary voltage, Ep...
#99 MCQ
When the winding c-d of the single-phase, 50 Hz, two-winding transformer is supplied from an AC current source of frequency 50 Hz, the rated voltage of 200 V (r...
#199 Fill in the Blanks
In a single-phase transformer, the total iron loss is 2500 W at nominal voltage of 440 V and frequency 50 Hz. The total iron loss is 850 W at 220 V and 25 Hz. T...
#253 MCQ