Electrical Engineering > GATE 2019 > Three-Phase Circuits
The magnitude of three-phase power supplied to a balanced star-connected load is 80 kW at 0.8 p.f. leading. The line voltage is 400 V, 50 Hz. The magnitude of the line current is _________ A (round off to one decimal place).

Correct : 144.0 to 144.5