Electrical Engineering > GATE 2019 > Electrical Instruments
The total impedance of the secondary winding, leads, and burden of a 5 A CT is 0.01 2. If the fault current is 20 times the rated primary current of the CT, the VA output of the CT is __________.

Correct : 95 to 105