Electrical Engineering > Gate 2019 > Fault Analysis
Five alternators each rated 5 MVA, 13.2 kV with 25% of reactance on its own base are connected in parallel to a
busbar. The short-circuit level in MVA at the busbar is _________.
Correct : 100