Electrical Engineering > GATE 2018 > Transformers
A 3-phase 900 kVA, 3 kV / (3 / √3) kV (∆/Y), 50 Hz transformer has primary (high voltage side) resistance per phase of 0.3 Ω and secondary (low voltage side) resistance per phase of 0.02 Ω. [cite: 107] Iron loss of the transformer is 10 kW. The full load % efficiency of the transformer operated at unity power factor is _______ (up to 2 decimal places).
Correct : 97.20
Similar Questions
Which one of the following options represents possible voltage polarities in a single-phase two winding transformer? Here, Vp is the applied primary voltage, Ep...
When the winding c-d of the single-phase, 50 Hz, two-winding transformer is supplied from an AC current source of frequency 50 Hz, the rated voltage of 200 V (r...
In a single-phase transformer, the total iron loss is 2500 W at nominal voltage of 440 V and frequency 50 Hz. The total iron loss is 850 W at 220 V and 25 Hz. T...