Electrical Engineering > GATE 2018 > Power System Stability
The per-unit power output of a salient-pole generator which is connected to an infinite bus, is given by the expression: P = 1.4 sin(δ) + 0.15 sin(2δ), where δ is the load angle. Newton-Raphson method is used to calculate the value of δ for P = 0.8 pu. If the initial guess is 30°, then its value (in degree) at the end of the first iteration is:
A
15°
B
28.48°
C
28.74°
D
31.20°

Correct : c

Similar Questions

In the system shown below, the generator was initially supplying power to the grid. A temporary LLLG bolted fault occurs at F very close to circuit breaker 1. T...
#1029 MCQ
As you grow older, an injury to your _________ may take longer to _________.
#3 MCQ
In a 500 m race, P and Q have speeds in the ratio of 3 ∶ 4. Q starts the race when P has already covered 140 m. What is the distance between P and Q (in m) whe...
#4 MCQ

Related Topics

No tags found

Unique Visitor Count

Total Unique Visitors

Loading......