Electrical Engineering > GATE 2018 > Power Flow Analysis
Consider the two bus power system network with given loads as shown in the figure. All the values shown in the figure are in per unit. The reactive power supplied by generator G1 and G2 are QG1 and QG2 respectively. The per unit values of QG1, QG2 and line reactive power loss Qloss respectively are:
A
5. 00, 12.68, 2.68
B
6.34, 10.00, 1.34
C
6.34, 11.34, 2.68
D
5.00, 11.34, 1.34

Correct : c