Electrical Engineering > GATE 2017 SET-2 > Transmission Lines
The nominal-π circuit of a transmission line is shown in the figure.
Impedance Z = 100∠80° Ω and reactance X = 3300 Ω. The magnitude of the characteristic impedance of the transmission line, in Ω, is ________. (Give the answer up to one decimal place.)

Correct : 406.2

Similar Questions

A 50 Hz, 275 kV line of length 400 km has the following parameters: Resistance, R=0.035 Ω/km; Inductance, L=1 mH/km; Capacitance, C=0.01 μF/km. The line is repr...
#179 Fill in the Blanks
In the figure shown, self-impedances of the two transmission lines are 1.5j p.u each, and Zm = 0.5j p.u is the mutual impedance. Bus voltages shown in the figur...
#255 MCQ
Consider a lossy transmission line with V1 and V2 as the sending and receiving end voltages, respectively. Z and X are the series impedance and reactance of the...
#371 MCQ