Electrical Engineering > GATE 2017 Set-1 > Synchronous Motors
A three-phase, 50Hz, star-connected cylindrical-rotor synchronous machine is running as a motor. The machine is operated from a 6.6 kV grid and draws current at unity power factor (UPF). The synchronous reactance of the motor is 30 Ω per phase. The load angle is 30°. The power delivered to the motor in kW is ____________. (Give the answer up to one decimal place).

Correct : 835 to 842

Similar Questions

A three-phase synchronous motor with synchronous impedance of 0.1+j0.3 per unit per phase has a static stability limit of 2.5 per unit. The corresponding excita...
#193 Fill in the Blanks
A star-connected 3-phase, 400 V, 50 kVA, 50 Hz synchronous motor has a synchronous reactance of 1 ohm per phase with negligible armature resistance. The shaft l...
#498 Fill in the Blanks
The induced emf in a 3.3 kV, 4 pole, 3-phase star connected synchronous motor is considered to be equal and in phase with the terminal voltage under no load con...
#1016 NAT

Related Topics

synchronous motor operation three phase motor star connected motor cylindrical rotor motor synchronous reactance calculation power factor motor motor load angle synchronous motor power GATE electrical engineering 2017 synchronous motor power calculation