Electrical Engineering > GATE 2016 SET-2 > Fault Analysis
Two identical unloaded generators are connected in parallel as shown in the figure. Both the generators are having positive, negative and zero sequence impedances of j0.4 p.u., j0.3 p.u. and j0.15 p.u., respectively. If the pre-fault voltage is 1 p.u., for a line-to-ground (L-G) fault at the terminals of the generators, the fault current, in p.u., is ________.

Correct : -j3.75

Similar Questions

Five alternators each rated 5 MVA, 13.2 kV with 25% of reactance on its own base are connected in parallel to a busbar. The short-circuit level in MVA at the b...
#62 Fill in the Blanks
The two-bus power system shown in figure (i) has one alternator supplying a synchronous motor load through a Y-ฮ” transformer. The positive, negative, and zero-s...
#206 Fill in the Blanks
The positive, negative and zero sequence impedances of a 125 MVA, three-phase, 15.5 kV, star-grounded, 50 Hz generator are j0.1 pu, j0.05 pu and j0.01 pu respec...
#384 Fill in the Blanks

Related Topics