Electrical Engineering > GATE 2016 SET-2 > Transformers
Three single-phase transformers are connected to form a delta-star three-phase transformer of 110 kV / 11 kV. The transformer supplies at 11 kV a load of 8 MW at 0.8 p.f. lagging to a nearby plant. Neglect the transformer losses. The ratio of phase currents in delta side to star side is
Correct : c
Similar Questions
Which one of the following options represents possible voltage polarities in a single-phase two winding transformer? Here, Vp is the applied primary voltage, Ep...
When the winding c-d of the single-phase, 50 Hz, two-winding transformer is supplied from an AC current source of frequency 50 Hz, the rated voltage of 200 V (r...
In a single-phase transformer, the total iron loss is 2500 W at nominal voltage of 440 V and frequency 50 Hz. The total iron loss is 850 W at 220 V and 25 Hz. T...