Electrical Engineering > GATE 2016 SET-2 > Power Factor Correction
The power consumption of an industry is 500 kVA, at 0.8 p.f. lagging. A synchronous motor is added to raise the power factor of the industry to unity. If the power intake of the motor is 100 kW, the p.f. of the motor is ________.

Correct : 0.316

Similar Questions

A three-phase cable is supplying 800 kW and 600 kVAr to an inductive load. It is intended to supply an additional resistive load of 100 kW through the same cabl...
#599 Fill in the Blanks
A single phase induction motor draws 12 MW power at 0.6 lagging power factor. A capacitor is connected in parallel to the motor to improve the power factor of t...
#833 NAT
The load shown in the figure absorbs 4 kW at a power factor of 0.89 lagging. Assuming the transformer to be ideal, the value of the reactance X to improve th...
#905 Fill in the Blanks