Electrical Engineering > GATE 2016 SET-2 > Fault Analysis
A 50 MVA, 10 kV, 50 Hz, star-connected, unloaded three-phase alternator has a synchronous reactance of 1 p.u. and a sub-transient reactance of 0.2 p.u. If a 3-phase short circuit occurs close to the generator terminals, the ratio of initial and final values of the sinusoidal component of the short circuit current is ________.

Correct : 5

Similar Questions

Five alternators each rated 5 MVA, 13.2 kV with 25% of reactance on its own base are connected in parallel to a busbar. The short-circuit level in MVA at the b...
#62 Fill in the Blanks
The two-bus power system shown in figure (i) has one alternator supplying a synchronous motor load through a Y-ฮ” transformer. The positive, negative, and zero-s...
#206 Fill in the Blanks
The positive, negative and zero sequence impedances of a 125 MVA, three-phase, 15.5 kV, star-grounded, 50 Hz generator are j0.1 pu, j0.05 pu and j0.01 pu respec...
#384 Fill in the Blanks

Related Topics

No tags found

Unique Visitor Count

Total Unique Visitors

Loading......