Electrical Engineering > GATE 2016 SET-2 > Transmission Lines
The inductance and capacitance of a 400 kV, three-phase, 50 Hz lossless transmission line are 1.6 mH/km/phase and 10 nF/km/phase respectively. The sending end voltage is maintained at 400 kV. To maintain a voltage of 400 kV at the receiving end, when the line is delivering 300 MW load, the shunt compensation required is
A
capacitive
B
inductive
C
resistive
D
zero

Correct : b