Electrical Engineering > GATE 2016 SET-2 > Protection
A power system with two generators is shown in the figure below. The system (generators, buses and transmission lines) is protected by six overcurrent relays R1 to R6. Assuming a mix of directional and non-directional relays at appropriate locations, the remote backup relays for R4 are
A
R1, R2
B
R2, R6
C
R2, R5
D
R1, R6

Correct : d