A three-phase, 50 Hz salient-pole synchronous motor has a per-phase direct-axis reactance (Xd) of 0.8 pu and a per-phase quadrature-axis reactance (Xq) of 0.6 pu. Resistance of the machine is negligible. It is drawing full-load current at 0.8 pf (leading). When the terminal voltage is 1 pu, per-phase induced voltage, in pu, is ________.
Correct : 1.456