Electrical Engineering > GATE 2015 SET-2 > Power Measurement
A 3-phase balanced load which has a power factor of 0.707 is connected to a balanced supply. The power consumed by the load is 5 kW. The power is measured by the two-wattmeter method. The readings of the two wattmeters are
A
3.94 kW and 1.06 kW
B
2.50 kW and 2.50 kW
C
5.00 kW and 0.00 kW
D
2.96 kW and 2.04 kW

Correct : a