Electrical Engineering > GATE 2015 SET-1 > Transformers
Two single-phase transformers T1 and T2 each rated at 500 kVA are operated in parallel. Percentage impedances of T1 and T2 are (1+j6) and (0.8+j4.8), respectively. To share a load of 1000 kVA at 0.8 lagging power factor, the contribution of T2 (in kVA) is ________.

Correct : 555.55

Similar Questions