Electrical Engineering > GATE 2014 SET-3 > Synchronous Generators
A non-salient pole synchronous generator having synchronous reactance of 0.8 pu is supplying 1 pu power to a unity power factor load at a terminal voltage of 1.1 pu. Neglecting the armature resistance, the angle of the voltage behind the synchronous reactance with respect to the angle of the terminal voltage in degrees is ________.
Correct : 32.4 to 34.0
Similar Questions
A 3-phase, 11 kV, 10 MVA synchronous generator is connected to an inductive load of power factor (√3/2) via a lossless line with a per-phase inductive reactance...
A three-phase cylindrical rotor synchronous generator has a synchronous reactance XS and a negligible armature resistance. The magnitude of per phase terminal v...
A single 50 Hz synchronous generator on droop control was delivering 100 MW power to a system. Due to increase in load, generator power had to be increased by 1...