Electrical Engineering > GATE 2014 SET-3 > Transformers
An open circuit test is performed on 50 Hz transformer, using variable frequency source and keeping V/f ratio constant, to separate its eddy current and hysteresis losses. The variation of core loss/frequency as function of frequency is shown in the figure
The hysteresis and eddy current losses of the transformer at 25 Hz respectively are
A
250 W and 2.5 W
B
250 W and 62.5W
C
312.5 W and 62.5 W
D
312.5 W and 250 W

Correct : b