Electrical Engineering > GATE 2014 SET-2 > Power Factor Correction
A single phase induction motor draws 12 MW power at 0.6 lagging power factor. A capacitor is connected in parallel to the motor to improve the power factor of the combination of motor and capacitor to 0.8 lagging. Assuming that the real and reactive power drawn by the motor remains same as before, the reactive power delivered by the capacitor in MVAR is ________.
Correct : 7
Similar Questions
A three-phase cable is supplying 800 kW and 600 kVAr to an inductive load. It is intended to supply an additional resistive load of 100 kW through the same cabl...
The power consumption of an industry is 500 kVA, at 0.8 p.f. lagging. A synchronous motor is added to raise the power factor of the industry to unity. If the po...
The load shown in the figure absorbs 4 kW at a power factor of 0.89 lagging.
Assuming the transformer to be ideal, the value of the reactance X to improve th...