A rolled I-section beam is supported on a 75 mm wide bearing plate as shown in the figure. The thicknesses of the flange and web of the I-section are 20 mm and 8 mm, respectively. The root radius of the I-section is 10 mm. Assume: material yield stress, fy = 250 MPa and partial safety factor for material, γmo = 1.10.
As per IS: 800-2007, the web bearing strength (in kN, round off to 2 decimal places) of the beam is _______.

Correct : 272.60 to 272.80