Chemical Engineering > GATE 2023 > Heat Exchangers
A perfectly insulated, concentric tube countercurrent heat exchanger is used to cool lubricating oil using water as a coolant (see figure below). Oil enters the outer annulus at a mass flow rate of 2 kg·s−1 with a temperature of 100 °C and leaves at 40 °C. Water enters the inner tube at a mass flow rate of 1 kg·s−1 with a temperature of 20 °C and leaves at 80 °C. Use specific heats of oil and water as 2089 J·kg−1·K−1 and 4178 J·kg−1·K−1, respectively. There is no phase change in both the streams. Under steady-state conditions, the number of transfer units (NTU) is _______ (in integer).

Correct : 1

Similar Questions

Hot oil at 110 ℃ heats water from 30 ℃ to 70 ℃ in a counter-current double-pipe heat exchanger. The flow rates of water and oil are 50 kg min−1 and 100...
#58 MCQ
A perfectly insulated double pipe heat exchanger is operating at steady state. Saturated steam enters the inner pipe at 100 °C and leaves as saturated water a...
#188 Fill in the Blanks
Stream A with specific heat capacity CPA = 2000 J/(kg K) is cooled from 90 °C to 45 °C in a concentric double pipe counter current heat exchanger having a heat...
#341 Fill in the Blanks