Chemical Engineering > GATE 2023 > Process Control
Level (β„Ž) in a steam boiler is controlled by manipulating the flow rate (𝐹) of the make-up (fresh) water using a proportional (P) controller. The transfer function between the output and the manipulated input is
β„Ž(𝑠)/𝐹(𝑠)=0.25(1βˆ’π‘ )/ 𝑠(2𝑠+1).
The measurement and valve transfer functions are both equal to 1. A process engineer wants to tune the controller so that the closed-loop response gives decaying oscillations under servo mode. Which one of the following is the CORRECT value of the controller gain to be used by the engineer?
A
0.25
B
2
C
4
D
6

Correct : d