Chemical Engineering > GATE 2018 > Heat Exchangers
A hot liquid is to be cooled in a 1-1 shell and tube heat exchanger from 80oC to 50oC.
Cooling water enters the tube side at 30oC, and exits at 45oC. The properties of the liquids
are constant. Also, the overall heat transfer coefficient is same for counter-current and co
current modes. The percentage saving in heat transfer area for counter-current option with
respect to the area of co-current option is __________ (rounded off to third decimal place).
Correct : 27.087
Similar Questions
Hot oil at 110 ℃ heats water from 30 ℃ to 70 ℃ in a counter-current double-pipe
heat exchanger.
The flow rates of water and oil are 50 kg min−1 and 100...
A perfectly insulated, concentric tube countercurrent heat exchanger is used to cool lubricating oil using water as a coolant (see figure below). Oil enters the...
A perfectly insulated double pipe heat exchanger is operating at steady state.
Saturated steam enters the inner pipe at 100 °C and leaves as saturated water a...