Biomedical Engineering > GATE 2020 > Power Factor Correction
Two loads are connected to AC supply mains as depicted in the figure. One load draws 10 kW whereas the other load of 10 kVA is operated at 0.6 pf lagging. To achieve an overall power factor of 0.9544 lagging, the nearest kV Ar rating of the capacitor bank needed to be connected across the supply mains is equal to _______.
A
3
B
5
C
7
D
9

Correct : a

Similar Questions

You should _________ when to say _________.
#2 MCQ
Two straight lines pass through the origin (x0, y0) = (0,0). One of them passes through the point (x1, y1) = (1,3) and the other passes through the point (x2,...
#3 MCQ
If p ∶ q = 1 ∶ 2 q ∶ r = 4 ∶ 3 r ∶ s = 4 ∶ 5 and u is 50% more than s, what is the ratio p ∶ u?
#4 MCQ

Related Topics

No tags found

Unique Visitor Count

Total Unique Visitors

Loading......