Two loads are connected to AC supply mains as depicted in the figure. One load draws 10 kW whereas the other load of 10 kVA is operated at 0.6 pf lagging. To achieve an overall power factor of 0.9544 lagging, the nearest kV Ar rating of the capacitor bank needed to be connected across the supply mains is equal to _______.
A
3
B
5
C
7
D
9

Correct : a