Agricultural Engineering > GATE 2017 > Cold Storage
In a cold storage, 10 metric ton of potato is to be brought down from 30 to 8°C storage temperature in 6 hours of air blast at the evaporator temperature of -10°C. Specific heat capacity of potato is 3.2 kJ/kg K. COP of the refrigeration cycle deployed is 4.2 with evaporator load extraction capacity of 210 kJ/kg. Neglecting the respiration load of potato, the refrigerant flow rate and compressor power requirement will be
A
A. 3.9 kg/min, 7.76 kW
B
B. 9.3 kg/min, 8.50 kW
C
C. 9.3 kg/min, 7.76 kW
D
D. 3.9 kg/min, 8.50 kW

Correct : c