Agricultural Engineering > GATE 2017 > Psychrometry
For a psychrometric ratio of 1.003 J/kg K, the latent heat of vaporization at the wet bulb temperature of 35°C is 2418.9 kJ/kg. The saturation vapour pressure is 19.7 kPa corresponding to the dry bulb temperature of 60°C. If the relative humidity of air is 20%, the saturation vapor pressure of the air at the wet bulb temperature in kPa will be

Correct : 5.5

Similar Questions

An air – water vapour mixture is at 35°C and normal atmospheric pressure with absolute humidity of 0.02 kg water vapour kg-1 dry air. Its humid volume in m3 kg-...
#440 NAT
Two kg mass of air at 40 °C with 0.023 kg water vapour per kg dry air is mixed with 3 kg mass of air at 20 °C with 0.008 kg water vapour per kg dry air to produ...
#523 NAT
Specific heat capacity of dry air and water vapour are 1.005 and 1.88 kJ kg-1K-1, respectively. In an energy conserving system, 1 kg s-1air at 30 °C with consta...